Main Panel question - sroxberg - 10-23-2016

I have a GE TM2010CCU  load panel with a 100 amp breaker.

It has 20 full spaces.

I don't have the manual but from what I reading online I cannot put 1/2 breakers in this to expand my number of circuits.

Is anyone familiar with this panel or GE panels, it was in the shop when I bought it.


RE: Main Panel question - JIMB49 - 10-23-2016

if you would have the "Q' line  it would accept the 1/2  breakers below is the link to ge reference
https://www.geindustrial.com/catalog/buylog/01_BuyLog2013_LoadCtrCircBreak.pdf


RE: Main Panel question - Phil Thien - 10-23-2016

It should list the number of spaces and the number of circuits. If the two numbers are the same then no doubles. If circuits > spaces you can figure out how many doubles.


RE: Main Panel question - Roly - 10-23-2016

(10-23-2016, 01:53 PM)Phil Thien Wrote: It should list the number of spaces and the number of circuits. If the two numbers are the same then no doubles. If circuits > spaces you can figure out how many doubles.

 It is listed as 20 spaces/ 20 circuits.    As Phil said no doubles.   Roly


RE: Main Panel question - sroxberg - 10-23-2016

Thanks for the confirmation, that is what I was thinking. Oh well, the Electrical company says that the feeder to the panel is already rated for 200 amps so it is just switching out the panel which will require a licensed pro, I'm not touching that job.


RE: Main Panel question - Mr_Mike - 10-23-2016

What is your particular need?

I can't see the average guy needing more than 100 amps in a shop.

If you just need more breaker space, just add a sub next to the existing. Way cheaper. You can put a 100 amp sub next to it just for the breaker space and feed it with a 60 amp breaker.

Way, way cheaper and you may find you are willing to do it yourself.

Added: Many main breaker panels can be used as subs by removing the bonding strap. You can get a 12 slot/22 breaker GE panel for about $60 from the big box stores.


RE: Main Panel question - GHR - 10-23-2016

(10-23-2016, 05:40 PM)Mr_Mike Wrote: If you just need more breaker space, just add a sub next to the existing.  Way cheaper.  You can put a 100 amp sub next to it just for the breaker space and feed it with a 60 amp breaker.  

Way, way cheaper and you may find you are willing to do it yourself.

Added:  Many main breaker panels can be used as subs by removing the bonding strap.  You can get a 12 slot/22 breaker GE panel for about $60 from the big box stores.

This is a reasonable solution.


RE: Main Panel question - crokett™ - 10-23-2016

I would add the sub.  It's going to be a whole lot less work (and much cheaper) than replacing the existing panel.

Edited to add, even if an electrician does it. It's something you can do yourself for 125 bucks or so in parts. We can talk you through it.


RE: Main Panel question - fredhargis - 10-24-2016

Another yes to adding a sub...not that hard, especially if you put it right next to the existing panel.


RE: Main Panel question - sroxberg - 10-25-2016

I only want and need a few extra breaker slots and the 100 amps should be fine. 

So If I drop a 60 Sub Panel about 10 feet away from the main panel running the wire in EMT what wire size and EMT size should I use?