1/2 power out - Gibbcutter - 06-03-2020

Just had an electrical storm blow through. Lost power in 3 breakers. Any idea what’s going on?


RE: 1/2 power out - Robert Adams - 06-03-2020

Assuming you reset them and still no power then they are toasted. But make sure to flip them off then back on. Some breakers regardless of brand will trip but the lever won't look like it has tripped.


RE: 1/2 power out - MauleSkinner - 06-03-2020

Are they all on the same side of the box?


RE: 1/2 power out - K. L. McReynolds - 06-03-2020

What he said. Another possibility is a fried ground/neutral or open circuits for those breakers.


RE: 1/2 power out - JTTHECLOCKMAN - 06-03-2020

Are they in a row?? Are they all on the same phase??  Maybe you lost a phase at transformer. What type breakers??  Are they ground fault or ark fault breakers??  Need some more info.


RE: 1/2 power out - Gibbcutter - 06-04-2020

Thanks for the feedback. Just got up and the power is back to 100%.


RE: 1/2 power out - TDKPE - 06-04-2020

Sounds like one phase conductor (of the two) is open.  Are the breakers that are unpowered on alternating rows in the panel?


RE: 1/2 power out - Gibbcutter - 06-04-2020

Someone told me I lost a leg.


RE: 1/2 power out - TDKPE - 06-04-2020

(06-04-2020, 06:27 AM)Gibbcutter Wrote: Someone told me I lost a leg.

In a 'normal' lighting and distribution panel, with two columns of breakers, each left-right pair of breakers is on alternating legs of incoming power.  So if the top two breakers, then the third two breakers, then fifth two, and so on (or second, fourth, sixth, etc.) are dead, you've lost a leg.  

Cycle the main breaker.  If that doesn't restore power, it's time to call the POCO.

Edit: I should add that it's not terribly unusual to lose a leg, or the neutral for that matter, which is way more hazardous than losing a leg. DW's sister lost a leg at her house due to a rodent chewing the underground cable. The POCO tied the dead side to the live side in the main panel, which restored power temporarily (except that no 240V loads had power), until they could come out and dig up her front yard to make the repair, which they did the next day.