Posts: 4,812
Threads: 0
Joined: Apr 2005
Location: Macomb, OK
I need to put in circuits for a tablesaw, bandsaw, and planer, all 5hp. Some people say to put in 40amp/#8, others say 30amp/#10 is fine. The machines will probably be about 40 feet from the panel. What does everyone think?
Posts: 1,932
Threads: 0
Joined: Feb 2008
09-01-2024, 12:32 AM
(This post was last modified: 09-01-2024, 12:35 AM by MstrCarpenter.)
A 5hp. air compressor probably draws more amps at start-up than the other equipment. They're usually less than 25 FLA. Check the data on the equipment you need to power and go higher from there.
Sign at N.E. Vocational School Cabinetmaking Shop 1976, "Free knowledge given daily... Bring your own container"
Posts: 12,596
Threads: 0
Joined: Aug 2003
Location: Wapakoneta, OH
I have a 5 HP SS that has about 30' of wire between it and the panel and it runs on #10 wire and a 30 amp breaker. MY DC (also 5 HP) is closer to 50' of wire and it's also on #10 wire and a 30 amp breaker. The DC really draws the juice on start up as it brings the impeller up to speed and I've never had a problem tripping the breaker. But I have seen some 5 HP tools spec a 40 amp circuit in the manual. I don't really see that as necessary, probably a CYA move by the vendor..
I started with absolutely nothing. Now, thanks to years of hard work, careful planning, and perseverance, I find I still have most of it left.
Posts: 12,858
Threads: 0
Joined: Jan 2010
Location: Lewiston, NY
(08-31-2024, 09:48 PM)blanning Wrote: I need to put in circuits for a tablesaw, bandsaw, and planer, all 5hp. Some people say to put in 40amp/#8, others say 30amp/#10 is fine. The machines will probably be about 40 feet from the panel. What does everyone think?
The Grizzly manual for my 5 hp bandsaw says a minimum 30 amp circuit with #10 gage wire. That's what I have it on, with a run of about 30 ft from the panel. 6 years or so, never a problem.
John
Posts: 4,812
Threads: 0
Joined: Apr 2005
Location: Macomb, OK
09-01-2024, 09:00 PM
(This post was last modified: 09-01-2024, 09:00 PM by blanning.)
(09-01-2024, 08:46 AM)jteneyck Wrote: The Grizzly manual for my 5 hp bandsaw says a minimum 30 amp circuit with #10 gage wire. That's what I have it on, with a run of about 30 ft from the panel. 6 years or so, never a problem.
John
After posting, I figured if I'm installing new power, I may as well go with #8 and 40 amps. It's more money but not that much more it looks like. On the other hand, if I put in #10, I can always pull out the wire and run #8 later if it becomes a problem.
I guess the best thing is to just do what the manual says.
Posts: 12,858
Threads: 0
Joined: Jan 2010
Location: Lewiston, NY
(09-01-2024, 09:00 PM)blanning Wrote: After posting, I figured if I'm installing new power, I may as well go with #8 and 40 amps. It's more money but not that much more it looks like. On the other hand, if I put in #10, I can always pull out the wire and run #8 later if it becomes a problem.
I guess the best thing is to just do what the manual says.
If you plan on running multiple machines at the same time on that line, then you will need a larger breaker and heavier wire. If it's just the bandsaw, however, I don't see why you would.
John
Posts: 39,993
Threads: 0
Joined: Apr 2007
(09-01-2024, 09:00 PM)blanning Wrote: After posting, I figured if I'm installing new power, I may as well go with #8 and 40 amps. It's more money but not that much more it looks like. On the other hand, if I put in #10, I can always pull out the wire and run #8 later if it becomes a problem.
I guess the best thing is to just do what the manual says.
I have never seen anyone go back with larger wire. If you plan on running one machine at a time the 30 amp breaker should be good or you need to plan on having an additional breaker to run whatever else you may run at the same time. Shop tools at my place are in a separate panel which can be powered off with by a single switch. I never worry about the wiring overheating.
Phydeaux said "Loving your enemy and doing good for those that hurt you does not preclude killing them if they make that necessary."
Phil Thien
women have trouble understanding Trump's MAGA theme because they had so little involvement in making America great the first time around.
Posts: 12,596
Threads: 0
Joined: Aug 2003
Location: Wapakoneta, OH
Give this some thought, I don't think there is a NEMA 40 amp plug/receptacle setup, they list a 30 amp, then it goes to 50 amps.
I started with absolutely nothing. Now, thanks to years of hard work, careful planning, and perseverance, I find I still have most of it left.
Posts: 1,992
Threads: 1
Joined: Aug 2016
(09-07-2024, 05:36 AM)fredhargis Wrote: Give this some thought, I don't think there is a NEMA 40 amp plug/receptacle setup, they list a 30 amp, then it goes to 50 amps.
Correct, but you can use a 50 amp receptacle on a 40 amp circuit or hard wire the saw. Roly
Posts: 5,619
Threads: 0
Joined: Nov 2004
This thread made me thing of something with the way my garage was wired up by the previous owner who would park an RV in there and I think someone ran a business too.
I have a 50A outlet wired to a 50A breaker. They also tapped into that same feed and installed a 20A outlet on the same breaker. Is there any safety issues having a 20A circuit on a 50A breaker? Just thinking of drawing more current than the outlet can handle without blowing the breaker. More in the even of a failure or short, not so much using a tool that pulls more than 20A. I would replace the outlet and wiring if I did that.
|