08-18-2015, 12:08 PM
Preview to the thread. I bought a new to me house last July. So we've been living there just over a year, but we'll call it two summers. The house was built in 2000. The previous owner stated on the paperwork that the compressor in the outside AC unit was replaced in 2013. I, and my AC man have verified that the compressor looks like a 2013 vintage.
I have a 40 amp (double) breaker coming off of the meter dedicated to the outside unit. One time, early in the summer (sometime in May?), LOML tells me that the AC is blowing hot air. Astutely notes that she doesn't hear the outside unit running. I go check the breaker and it's tripped. So I flip it back on. Unit purrs to life and blows cold.
Fast forward to last weekend. We were gone on a trip and I set the thermostat to 80 before we left. Came back home Sunday night and find the house is 87. The air handler is blowing it's heart out, but the outside unit is not on. Check the breaker first thing. It's tripped. Flipped it back on. Fired to life and blew cool air.
So yesterday I decided to do some investigation. I put my amp clamp on each wire going to the unit. I was getting 27-28 amps at start up, leveling off to 22-24 amps steady. Shouldn't be anywhere near enough to trip a 40 amp breaker. My question is, why the randomness? The starter capacitor looked original to the unit. The contactor looked newer.
I sure don't want to go spending money for the heck of it. On the other hand, being proactive often comes out a little cheaper. And it's going to be at least 102 for three straight days this weekend.
Why's the breaker tripping at random? Would you do anything about it?
I have a 40 amp (double) breaker coming off of the meter dedicated to the outside unit. One time, early in the summer (sometime in May?), LOML tells me that the AC is blowing hot air. Astutely notes that she doesn't hear the outside unit running. I go check the breaker and it's tripped. So I flip it back on. Unit purrs to life and blows cold.
Fast forward to last weekend. We were gone on a trip and I set the thermostat to 80 before we left. Came back home Sunday night and find the house is 87. The air handler is blowing it's heart out, but the outside unit is not on. Check the breaker first thing. It's tripped. Flipped it back on. Fired to life and blew cool air.
So yesterday I decided to do some investigation. I put my amp clamp on each wire going to the unit. I was getting 27-28 amps at start up, leveling off to 22-24 amps steady. Shouldn't be anywhere near enough to trip a 40 amp breaker. My question is, why the randomness? The starter capacitor looked original to the unit. The contactor looked newer.
I sure don't want to go spending money for the heck of it. On the other hand, being proactive often comes out a little cheaper. And it's going to be at least 102 for three straight days this weekend.
Why's the breaker tripping at random? Would you do anything about it?