No expert here, but been there, done that. You either need a new tank because the bladder is busted out, or you don't have enough air in the bladder. I'm thinking the former.
Credo Elvem ipsum etiam vivere
Non impediti ratione cogitationis
Posts: 38,525
Threads: 0
Joined: Feb 2002
Location: East Texas
there's a valve on the top of the tank. let just a hair bit of air out, if you get water instead of air, your tank's bladder is busted.
Reality is that which, when you stop believing in it, doesn't go away. - Philip K. Dick
Mark
Posts: 22,713
Threads: 0
Joined: Feb 2005
Location: Regina Saskatchewan Canada
You have leaks and one of them is either the drop pipe to the pump or its check valve.
Blackhat
Bad experiences come from poor decisions. So do good stories.
Posts: 5,733
Threads: 2
Joined: Dec 2004
Location: Fort Worth
Check the bladder Schrader for water and then if it's good turn the pump off empty the tank leave the valve open and set the air pressure in the bladder to 38lbs. Pressure tank pressure Is 2 lbs below the start pressure of the pump.
If you have air gurgling in the filter housing you may be pulling air back from where ever the other pipe goes. I'd like to see a valve on the pipe going down so you can isolate that output during service and testing.
You may also have a leaking check valve in the pump allowing water to drain back into the well and suck air from the house or where ever that pipe goes to.
I'm no expert but have have a fair bit of experience with Wells and pumps.