Looks like 1-1/4" Schedule 80 minimum, good for up to six 4-gauge THHN/THWN or XHHW conductors. You need Sch. 80 where it comes out of the ground.
And you don't need the equipment ground to be as large as the phase conductors; it depends on the size of the overcurrent protection for those phase conductors, though. 8-gauge copper equipment grounding conductor is good to 100A circuit ampacity. That's all assuming this is a feeder to a subpanel or load, not service conductors to a dwelling unit.
(03-09-2017, 01:29 PM)DieselDennis Wrote: Plan on pulling three or four #4 coppers. Not sure how many yet. Haven't asked that question to the city inspector.
If it's a feeder to an outbuilding, the requirement for 4 conductors has been in place since I believe the 1996 cycle, so it's unlikely your AHJ is working to an older book, one which allowed 3-wire feeders. And either way, you'd need a grounding electrode system, usually two ground rods driven vertically full depth, 6 ft or more apart.
Subpanels within the same building have needed 4 conductors for as far back as I know, at least on grounded systems.
Tom
“This place smells like that odd combination of flop sweat, hopelessness, aaaand feet"
Posts: 2,742
Threads: 0
Joined: Jan 2010
Might just as well go to 2". A lot easier to pull wires. Add a pull wire for future "just in case".