(02-17-2018, 03:57 PM)dgman Wrote: I am wiring a bathroom fan to a 20 amp circuit. The incoming wires are 12 gauge but the fan wires are much smaller (14 or 16 guage) . Is there are problem with the smaller wires being connectedfd to the 12 guage wire on the 20 amp circuit?
Thanks
No. Think of plugging in a table lamp or clock, those are 16 or 18 ga. . All of your lighting fixtures will be way smaller than 14 or 12 gauge house. Make sure the connections are secure by pulling on the wires after they are connected, sometimes going between the 12 and 16 ga. is problematic. Roly
Posts: 1,674
Threads: 0
Joined: Feb 2003
Practically speaking there should not be a problem. The only issue would be if the fixture would normally draw more current then the circuit was designed for (not likely with a bathroom light; even if it had a vent fan). I believe there is an NEC limitation on the length of 18AWG fixture wire that can be connected to a 12AWG branch circuit. but it is many, many feet (something like 50 feet). Basically the NEC assumes the fixture wire is designed to carry the load of the fixture itself. It doesn't really care if the fixture “burns up” – the Code is more concerned that the branch circuit is properly sized with the proper over-current protection.
Posts: 16,604
Threads: 0
Joined: Oct 2002
Location: Ra-cha-cha, NY
What Roly said. The leads are part of a listed (UL, CSA) assembly, and as such, they were tested to handle a short circuit or ground fault long enough to trip the breaker and clear the fault. And carry the design full-load current of the unit continuously, of course. Like a table lamp can.
Tom
“This place smells like that odd combination of flop sweat, hopelessness, aaaand feet"
Posts: 6
Threads: 0
Joined: Jan 2017
Haven't you consulted a professional to get this done easily.
Posts: 5,733
Threads: 2
Joined: Dec 2004
Location: Fort Worth
(02-17-2018, 03:57 PM)dgman Wrote: I am wiring a bathroom fan to a 20 amp circuit. The incoming wires are 12 gauge but the fan wires are much smaller (14 or 16 guage) . Is there are problem with the smaller wires being connectedfd to the 12 guage wire on the 20 amp circuit?
Thanks
No, no problem at all that's normal. You could run a circuit with 8 ga wire and all is good. It's when the demand of the installed fixture needs more than the circuit can handle it's an issue.
The wires in your house are sized for their length and their amp capacity. So longer runs will have bigger wires than would be needed for a very short run. Simplified answer but gets the point across. Like having a 6 lane freeway and only using one lane of it.