I was working on a job this week where they were adding VFDs to some equipment with 25 year old 3 phase motors. These motors have been in daily use and working just fine since installation. Here comes the risk of using a VFD on an old motor; one of them worked OK, but the other tripped out showing ground fault as soon as the drive was started up. It was temporarily reconnected to line voltage and a new drive rated motor ordered.
Sometimes you win and sometimes you loose using drives on old motors. The motor insulation is seeing voltages as high as 1,000 volts. It was designed for 480. Of course the switching cycle of the transistors can be in the megahertz range. That doesn’t help the older motor either.
I just thought I would mention this for those who are considering old three phase equipment when we live in a single phase world.
That motor would probably run on a mechanical rotophase. It is anybody's guess as to how much longer it would have run. An electronic mega ohm meter shows a dead short, but it works on the same principle as the drive. A regular ohm meter shows it being just fine.
Sometimes you win and sometimes you loose using drives on old motors. The motor insulation is seeing voltages as high as 1,000 volts. It was designed for 480. Of course the switching cycle of the transistors can be in the megahertz range. That doesn’t help the older motor either.
I just thought I would mention this for those who are considering old three phase equipment when we live in a single phase world.
That motor would probably run on a mechanical rotophase. It is anybody's guess as to how much longer it would have run. An electronic mega ohm meter shows a dead short, but it works on the same principle as the drive. A regular ohm meter shows it being just fine.