Posts: 12,605
Threads: 0
Joined: Aug 2003
Location: Wapakoneta, OH
09-20-2021, 03:26 PM
(This post was last modified: 09-20-2021, 03:30 PM by fredhargis.)
Deleted, I'll leave the explanation to the real sparkys.
I started with absolutely nothing. Now, thanks to years of hard work, careful planning, and perseverance, I find I still have most of it left.
Posts: 1,998
Threads: 1
Joined: Aug 2016
Don't delete it Fred, you were correct. Separate neutrals required after the gfci and also they cannot be grounded again after the gfci. The phase current and neutral current must be the same or it will trip. Roly
Posts: 58
Threads: 0
Joined: Jun 2018
Location: Eye-Da-Hoe
Thank you both. That was what I figured, but I was wishing in the one hand but the other hand filled up first.
I will replace with a couple runs of two conductor.
Posts: 2,201
Threads: 1
Joined: Oct 2003
But a 240 volt gfci breaker protects both legs??
Switch from the “breakers” to a single breaker.
He needed to do this anyway if he was sharing the neutral, or tie the handles together.
Wouldn’t this work?
Posts: 16,604
Threads: 0
Joined: Oct 2002
Location: Ra-cha-cha, NY
You can also run a multiwire circuit (shared neutral) and put a blank face GFCI at each load. I don't know how far apart the loads are, but wherever they split, or at the two loads after the split, you can use one of these to provide the same protection. The neutral has to split off with each hot, of course. About $20 each, and same form factor as any standard device.
[attachment=37790]
Tom
“This place smells like that odd combination of flop sweat, hopelessness, aaaand feet"
Posts: 12,605
Threads: 0
Joined: Aug 2003
Location: Wapakoneta, OH
<p>
(09-20-2021, 04:06 PM)srv52761 Wrote: But a 240 volt gfci breaker protects both legs??
Switch from the “breakers” to a single breaker.
He needed to do this anyway if he was sharing the neutral, or tie the handles together.
Wouldn’t this work?
<br></p><p><br></p><p>Help me out here guys. Does this suggest you can run 2-120V GFCI circuits using a 240V GFCI breaker with 1 neutral? <br></p>
I started with absolutely nothing. Now, thanks to years of hard work, careful planning, and perseverance, I find I still have most of it left.