What zone valve? They come in normally open and normally closed. Power causes them to change position.
Be glad to help you through troubleshooting this.
Blackhat
Bad experiences come from poor decisions. So do good stories.
Posts: 22,712
Threads: 0
Joined: Feb 2005
Location: Regina Saskatchewan Canada
I’ll try and put the pieces together.
You said the valves are closed. Assuming you mean normally close, when 24 v is present, the valve is open and allowing water to the emitters. You said the valve has 27v, the upstairs is heating. The valve is working as it should.
You said you measured 0 volts upstairs. I presume you meant at the thermostat connections. 0 volts means the thermostat switch is closed or the wires are shorted together somewhere between the t stat and the valve. I will assume there is no zone control panel between the tstat and the valve. Disconnect the wires from the 2nd floor stat and wait a half hour. The emitters on that floor should start to cool. If not, disconnect the wires from the valve and again wait to see if things cool off.
Blackhat
Bad experiences come from poor decisions. So do good stories.
Posts: 1,936
Threads: 0
Joined: Feb 2008
The zero volt reading at the thermostat may indicate that the common wire (blue or sometimes brown, purple or black) is not connected in the basement. It's not needed there to control the heat, cool or fan functions because they're just single pole switches. A common would be necessary to provide power for thermostats with clocks, timers and/or wi-fi.
I'm most familiar with Taco zone valves. Here's some of what I've learned over the years;
It can take over a full minute for the valve to open when power is connected to #1 & #2. That's also when #3 is energised (from #2) to tell your boiler to turn on.
If the valve is fully closed, the manual lever will leave a serious indentation in your thumb when you use it to open the valve. (If it doesn't, the valve may not be fully closing.)
It is not uncommon for a new valve to smoke during the first few cycles. It is not the factory installed "magic smoke", it's just the heater cooking some wax residue left behind during manufacturing.
Sign at N.E. Vocational School Cabinetmaking Shop 1976, "Free knowledge given daily... Bring your own container"
Posts: 403
Threads: 0
Joined: Sep 2003
THANK YOU, ALL!
After hours of trouble shooting, we determined that there must be a short in the wiring.
A lot of wire from basement to second floor and we had to cut "hand-size" holes in the drywall but we found the problem.
First, we discovered mice droppings and then pulled some wire out without insulation. Black burn on red.
All new wire from furnace to thermostat! Second floor heat is under control!!
Again, thanks for responding to my post and I wish you all a HAPPY THANKSGIVING!