(08-24-2020, 04:30 PM)TDKPE Wrote: The overload portion of the control is in the control. The little blue button.
But if you push the button and you don't hear the control clicking strongly, and releasing with the stop button, it sounds like there's an incoming power problem. Check the top connections (L1 and L3), as they can loosen with use. You need to get in there with your multimeter.
It's also possible the overload is tripped, though I don't know why it would trip when the saw isn't running. A tripped O/L relay will prevent the start button from closing the main contactor since it's contact set is in series with the start/stop control. BUT, it should be set to 'Auto' mode (the little dial in the middle). If it's defective, nothing will happen when you push the start button.
There should be no other junction box and/or O/L device between the control and the motor.