I just installed a laundry sink in my basement. I used a washer hook up for water, and the drain plumbing was right there.
There are 2 outlets very close. How far do they need to be from the sink? I can raise them higher on the wall- not much option left or right
Posts: 1,996
Threads: 1
Joined: Aug 2016
(09-24-2017, 02:08 PM)goaliedad Wrote: I just installed a laundry sink in my basement. I used a washer hook up for water, and the drain plumbing was right there.
There are 2 outlets very close. How far do they need to be from the sink? I can raise them higher on the wall- not much option left or right
I do not think there is a minimum distance but must be gfci if within 6'. Think of the vanity in a bathroom, outllets, are very close. Try to keep them out of a splash zone. Roly
Posts: 16,604
Threads: 0
Joined: Oct 2002
Location: Ra-cha-cha, NY
I'm not aware of any restrictions on receptacles in the vicinity of a laundry sink, other than GFCI protection. Which you'll have anyway, since it's presumably in an unfinished basement.
In fact, most such language regarding receptacles near sinks are the opposite - they're required to be within a certain distance (which depends on function and location, like bathrooms vs kitchens).
Those distances (to sinks and between each other) are along a horizontal line, by the way, with vertical location within a different range. So even if vertical location was a question, it has nothing to do with the horizontal location from a plumb line to the counter end, sink edge, each other, etc.