(10-13-2021, 10:48 AM)TDKPE Wrote: This has been nagging my brain - it's possible it's a three-phase motor, which will have 4 blades (three hots and an equipment ground). Plug would be either a 15-20P or a 15-30P, as a 5 hp three-phase only requires a 20A circuit at 240V. That saw is available new with either a single-phase or a three-phase motor.
That, or it's a twistlock like BloomingtonMike has, or it's both twist-lock and three-phase. If it's single-phase but with a twist-lock plug (L6-30P), it's an easy change to the straight blade equivalent (6-30P).
Edit: OR, it's a 30A dryer plug (NEMA 10-30P or 14-30P). Or a 50A range plug (NEMA 10-50P or 14-50P). Or something even more inappropriate.
You really need to tell us what the motor nameplate says, or post a picture of it. What the manual says may or may not be relevant, as the motor could have been replaced, and the manual may cover both types of motors. The motor nameplate will tell you everything you need to know.
That is the first thing I though of when I read 230V. We had a lot of 230V 3 phase stuff in our old lab building.
(10-13-2021, 03:39 PM)jteneyck Wrote: That is the first thing I though of when I read 230V. We had a lot of 230V 3 phase stuff in our old lab building.
John
Also my thought. There are also other 200-odd volt 3ph motors like 208v.
OP : how many ‘blades’ are there on the machine’s plug? 3? 4?
What does the motor data plate say? There should be a voltage and phase notation on the data plate (and current draw).
Any time I come across a 30 amp, 4 pole twist lock (either plug or receptacle), I always verify if it's single or three phase. They are different configurations, but so similar that if either is slightly worn they can be mated together. 3 phase equipment on single phase, and single phase equipment on 3 phase will let the magic smoke out. If that's the worst thing that happens, you're lucky because that lesson could cost a lot more.
Sign at N.E. Vocational School Cabinetmaking Shop 1976, "Free knowledge given daily... Bring your own container"
Same here. I’m a bit like Ben Afleck’s character in The Accountant in that I need to see something through or I get all wonky - and this is still hanging out there.
Tom
“This place smells like that odd combination of flop sweat, hopelessness, aaaand feet"
Sorry to leave y'all hanging. Busy weekend bringing home the x31 and some other unexpected gifts from my friend. Here are the plate, the plug, and what the motor looks like.
Eric Bruns
Licensed Psychologist
Aspiring amateur woodworker
10-18-2021, 03:49 PM (This post was last modified: 10-19-2021, 08:13 AM by TDKPE.)
That motor is single-phase, 220V (import), and just under 16A FLA. Technically, you can run it on a 20A circuit. 2.2kW converts to 3 hp.
The receptacle is a L6-20R, meaning it's single-phase, 250V rated, 20A, grounded, and locking. The plug you have is a NEMA 6-15R, meaning it's single-phase, 250V rated, 15A, grounded, but obviously not locking. It's not the correct plug for the tool (the 15A part), and obviously won't fit the receptacle.
You can simply change the plug to a NEMA L6-20P and be done with it, if you want to stay with locking plugs.
But I thought you said you had 30A circuits for your 240V tools. Never mind - I must have been thinking of another thread.
Edit: Upon rereading this thread, I got the idea of 30A from - wait for it - me. I looked up the saw, and the web site only shows 5 hp single- or three-phase as the current offering, which normally requires 30A or greater.
Tom
“This place smells like that odd combination of flop sweat, hopelessness, aaaand feet"