The electrical supply line coming out of the drywall ceiling into the top of the heater isn’t in conduit.
What’s involved in removing the connection at the top of the hot water heater in order to slide conduit over the Romex?
Gary

Please don’t quote the trolls.
Liberty, Freedom and Individual Responsibility
Say what you'll do and do what you say.
Reply
#7
Unscrew the cover plate, probably untwist wire nuts, unscrew the equipment ground. (Edit: probably an untwist also, not an unscrew - all pretty simple).

Assuming 240v, #10 10-2wg.

If so, you would need 3/4” flexible probably??
If it is 10-3wg then I think you’ll need to go to a1” conduit.
(@53% fill... if I read it correctly, someone else could correct me).

Edit:  if you want a more reasonable conduit size, 1/2”, consider adding a junction box at the ceiling and transitioning to thhn
Reply
#8
Why?




........................17.................
Blackhat

Bad experiences come from poor decisions. So do good stories. 


Reply
#9
No one here uses conduit.

But then again, no one ever uses a stress connector either.
Reply
#10
(12-14-2019, 11:33 PM)daddo Wrote: No one here uses conduit.

But then again, no one ever uses a stress connector either.

Must be a local code as they want it here also.   They are normally open at the top, conduit box connector on top of WH .  Just a sleeve for protection ?   Roly
Reply


Forum Jump:


Users browsing this thread: 1 Guest(s)

Product Recommendations

Here are some supplies and tools we find essential in our everyday work around the shop. We may receive a commission from sales referred by our links; however, we have carefully selected these products for their usefulness and quality.