220V plug wire question - Printable Version +- Woodnet Forums (https://forums.woodnet.net) +-- Thread: 220V plug wire question (/showthread.php?tid=7374595) Pages:
1
2
|
220V plug wire question - TyG - 12-26-2023 Hey all, I am putting in a 220v plug for a Lincoln BuzzBox welder. 50amp breaker. I would like to run across a two car garage, say 30' total run. I was planning on using 6 AWG wire for the two hots. Should I also use 6 AWG for ground wire also? RE: 220V plug wire question - JosephP - 12-26-2023 Pretty sure if you buy 6/2 with ground that ground is 10 gauge. Are you pulling individual strands or buying premade 6/2? RE: 220V plug wire question - TyG - 12-26-2023 (12-26-2023, 02:41 PM)JosephP Wrote: Pretty sure if you buy 6/2 with ground that ground is 10 gauge. I bought a 2 foot sectin of 6/3 w/ground just to get a quick job done, but it looks like it would be way cheaper to run individual. What gauge ground would be recommended? I was honestly thinking that I needed 6. RE: 220V plug wire question - Roly - 12-26-2023 (12-26-2023, 02:52 PM)TyG Wrote: I bought a 2 foot sectin of 6/3 w/ground just to get a quick job done, but it looks like it would be way cheaper to run individual. What gauge ground would be recommended? I was honestly thinking that I needed 6. Joseph was correct #10 for the ground wire. IF the ground is just used as a ground and not as a neutral. Roly RE: 220V plug wire question - fixtureman - 12-26-2023 A buzzbox is 30 amps you would need a 10 gauge for 50 feet. RE: 220V plug wire question - Snipe Hunter - 12-26-2023 Your ground needs to carry the same current at your hot's and neutral, otherwise your ground becomes a fuse. So they have to be sized the same. RE: 220V plug wire question - Roly - 12-26-2023 (12-26-2023, 08:29 PM)Snipe Hunter Wrote: Your ground needs to carry the same current at your hot's and neutral, otherwise your ground becomes a fuse. So they have to be sized the same. What does the NEC say ? If it is just used as a equipment ground use a 10 ga for 60 amp breaker circuit. Roly NEC 250.122 RE: 220V plug wire question - kencombs - 12-27-2023 Hey all, I am putting in a 220v plug for a Lincoln BuzzBox welder. 50amp breaker. I would like to run across a two car garage, say 30' total run. I was planning on using 6 AWG wire for the two hots. Should I also use 6 AWG for ground wire also? I'm not an expert by any means, but strongly suggest that you read the NEC section on welder circuits, Article 630. My AC/DC buzzbox is running on a NEC-legal circuit of 3 10AWG, THNN conductors. Red Black and green. Duty cycle is everything with sizing circuits for welders. RE: 220V plug wire question - Roly - 12-28-2023 (12-27-2023, 06:33 PM)kencombs Wrote: Hey all, You are correct for a commercial shop, BUT in a residential situation where the house may be sold and a new owner plugs something like a dryer into the outlet, What would happen to the wiring ? Extra crispy comes to mind. Roly RE: 220V plug wire question - kencombs - 12-28-2023 As long as the breaker is sized for the wire the breaker opens. No harm no foul |