Posts: 1,189
Threads: 0
Joined: Dec 2009
Hey all,
I am putting in a 220v plug for a Lincoln BuzzBox welder. 50amp breaker. I would like to run across a two car garage, say 30' total run. I was planning on using 6 AWG wire for the two hots. Should I also use 6 AWG for ground wire also?
Posts: 18,960
Threads: 0
Joined: Jul 2002
Location: Ohio
Pretty sure if you buy 6/2 with ground that ground is 10 gauge.
Are you pulling individual strands or buying premade 6/2?
Posts: 1,189
Threads: 0
Joined: Dec 2009
(12-26-2023, 02:41 PM)JosephP Wrote: Pretty sure if you buy 6/2 with ground that ground is 10 gauge.
Are you pulling individual strands or buying premade 6/2?
I bought a 2 foot sectin of 6/3 w/ground just to get a quick job done, but it looks like it would be way cheaper to run individual. What gauge ground would be recommended? I was honestly thinking that I needed 6.
Posts: 1,996
Threads: 1
Joined: Aug 2016
12-26-2023, 04:26 PM
(This post was last modified: 12-26-2023, 04:28 PM by Roly.)
(12-26-2023, 02:52 PM)TyG Wrote: I bought a 2 foot sectin of 6/3 w/ground just to get a quick job done, but it looks like it would be way cheaper to run individual. What gauge ground would be recommended? I was honestly thinking that I needed 6.
Joseph was correct #10 for the ground wire. IF the ground is just used as a ground and not as a neutral. Roly
Posts: 4,894
Threads: 0
Joined: May 2010
A buzzbox is 30 amps you would need a 10 gauge for 50 feet.
Posts: 64,647
Threads: 3
Joined: Feb 2007
Location: Merryland
Your ground needs to carry the same current at your hot's and neutral, otherwise your ground becomes a fuse. So they have to be sized the same.
Posts: 1,996
Threads: 1
Joined: Aug 2016
(12-26-2023, 08:29 PM)Snipe Hunter Wrote: Your ground needs to carry the same current at your hot's and neutral, otherwise your ground becomes a fuse. So they have to be sized the same.
What does the NEC say ? If it is just used as a equipment ground use a 10 ga for 60 amp breaker circuit. Roly
NEC 250.122
Posts: 246
Threads: 0
Joined: Sep 2004
Hey all,
I am putting in a 220v plug for a Lincoln BuzzBox welder. 50amp breaker. I would like to run across a two car garage, say 30' total run. I was planning on using 6 AWG wire for the two hots. Should I also use 6 AWG for ground wire also?
I'm not an expert by any means, but strongly suggest that you read the NEC section on welder circuits, Article 630. My AC/DC buzzbox is running on a NEC-legal circuit of 3 10AWG, THNN conductors. Red Black and green.
Duty cycle is everything with sizing circuits for welders.
Posts: 1,996
Threads: 1
Joined: Aug 2016
(12-27-2023, 06:33 PM)kencombs Wrote: Hey all,
I am putting in a 220v plug for a Lincoln BuzzBox welder. 50amp breaker. I would like to run across a two car garage, say 30' total run. I was planning on using 6 AWG wire for the two hots. Should I also use 6 AWG for ground wire also?
I'm not an expert by any means, but strongly suggest that you read the NEC section on welder circuits, Article 630. My AC/DC buzzbox is running on a NEC-legal circuit of 3 10AWG, THNN conductors. Red Black and green.
Duty cycle is everything with sizing circuits for welders.
You are correct for a commercial shop, BUT in a residential situation where the house may be sold and a new owner plugs something like a dryer into the outlet, What would happen to the wiring ? Extra crispy comes to mind. Roly
Posts: 246
Threads: 0
Joined: Sep 2004
As long as the breaker is sized for the wire the breaker opens. No harm no foul