Pretty sure if you buy 6/2 with ground that ground is 10 gauge.
Are you pulling individual strands or buying premade 6/2?
Posts: 4,893
Threads: 0
Joined: May 2010
A buzzbox is 30 amps you would need a 10 gauge for 50 feet.
Posts: 64,647
Threads: 3
Joined: Feb 2007
Location: Merryland
Your ground needs to carry the same current at your hot's and neutral, otherwise your ground becomes a fuse. So they have to be sized the same.
Posts: 246
Threads: 0
Joined: Sep 2004
Hey all,
I am putting in a 220v plug for a Lincoln BuzzBox welder. 50amp breaker. I would like to run across a two car garage, say 30' total run. I was planning on using 6 AWG wire for the two hots. Should I also use 6 AWG for ground wire also?
I'm not an expert by any means, but strongly suggest that you read the NEC section on welder circuits, Article 630. My AC/DC buzzbox is running on a NEC-legal circuit of 3 10AWG, THNN conductors. Red Black and green.
Duty cycle is everything with sizing circuits for welders.
Posts: 246
Threads: 0
Joined: Sep 2004
As long as the breaker is sized for the wire the breaker opens. No harm no foul