I got Ken Vick's mega jointer running today with the upgraded static phase converter he bought for it. It comes up to speed in 3 seconds now and seems to run very smoothly. I wired it so we could use the machine's normal on/off switches. This SPC replaces a lower rated unit. When I installed that one I couldn't get power to the motor and traced it to a thermal overload on the contactor. I bypassed the contactor, temporarily, and the contactor closed when I pushed the start button and the motor started. I didn't fool with the overload today when I installed the new SPC, but I'd like to resolve the issue for peace of mind.
The contactor is a Telemecanique, made in USA which I didn't expect with that name:
Attached at the bottom of the contactor is this overload relay:
What's confusing to me is that the relay is rated for a normal range of 5.5 to 8 amps (now set at 8 amps, as I found it), but the motor has a FLA rating of 11.2 amps and draws around 10 amps when running with no load except turning the cutterhead. There is a reset button on the relay, the red button at the right in the photo, but it won't reset when I push it. The wires now connected to T1, T2, and T3 on the contactor were connected to the 3 lugs on the overload relay until I bypassed it.
The former owner ran it on 230 V 3 phase power. We're running it on 220V single phase power through a static phase converter. He claims it ran fine. If so, the relay must have been the appropriate size, though it seems undersized to me. This is a new motor, but of the same 5 HP rating and amp. draw (actually, marginally lower) as the one it replaced.
Anyone have any ideas of what's going on here? Any input is appreciated. Thanks in advance.
John
The contactor is a Telemecanique, made in USA which I didn't expect with that name:
Attached at the bottom of the contactor is this overload relay:
What's confusing to me is that the relay is rated for a normal range of 5.5 to 8 amps (now set at 8 amps, as I found it), but the motor has a FLA rating of 11.2 amps and draws around 10 amps when running with no load except turning the cutterhead. There is a reset button on the relay, the red button at the right in the photo, but it won't reset when I push it. The wires now connected to T1, T2, and T3 on the contactor were connected to the 3 lugs on the overload relay until I bypassed it.
The former owner ran it on 230 V 3 phase power. We're running it on 220V single phase power through a static phase converter. He claims it ran fine. If so, the relay must have been the appropriate size, though it seems undersized to me. This is a new motor, but of the same 5 HP rating and amp. draw (actually, marginally lower) as the one it replaced.
Anyone have any ideas of what's going on here? Any input is appreciated. Thanks in advance.
John